Smart Meter Interface (Iskra MT 174) #18725

Closed Answered by kk98kk
kk98kk asked this question in Q&A
May 25, 2023 · 3 comments · 9 replies
Discussion options

You must be logged in to vote

Thank you for information to write in the console: sensor53 d1. I got the right values. After I changed script from

>D
>B
->sensor53 r
>M 1
+1,3,o,0,300,STROM,1,100,2F3F210D0A
1,1-0:1.8.1*255(@1,Total Consumed,KWh,Total_in,3
1,1-0:2.8.1*255(@1,Total Delivered,KWh,Total_out,3
1,1-0:0.0.0*255(@#),Meter Number,,Meter_number,0
#

to this:

>D
>B
->sensor53 r
>M 1
+1,3,o,0,300,STROM,1,100,2F3F210D0A
1,1-0:1.8.0*255(@1,Total Consumed,KWh,Total_in,3
1,1-0:2.8.0*255(@1,Total Delivered,KWh,Total_out,3
1,1-0:16.7.0*255(@1,Current Consumption,KWh,Power_cur,3
1,0-0:C.1.0*255(@#),Meter Number,,Meter_number,0
#

it worked perfect for me.
I don´t know if only my Iskra MT174 has this protocoll or everyone…